I am trying to find a ball park figure for the heat rejection of a 150 ton chiller system. Anybody have any insite or experience with these systems. It is made by Fulton Thermal Corp.
Cory McKnight Design Engineer ACCO Engineered Systems 1700 Industrial Road San Carlos CA 94070 Tel: 650-631-5977 Fax:650-594-4915
| | Replies:
|
| Yooper22 | "Re(1):emergency heat" , posted Fri 6 Feb 16:52  
Ball park figure answer is in the question. 150 Tons X 12,000 = aproximate heat rejection. That ball park figure would be around 1,800,000 BTU's per hour at or near full load.
BS is biodegradeable Truth is not.
|
| | energy | "Re(2):emergency heat" , posted Wed 12 Jan 15:49  
It is customary to add 10-20% on the figure above. and if it is an absorbtion chiller you may want to chech with the factory, it's much more.