I am trying to find a ball park figure for the heat rejection of a 150 ton chiller system. Anybody have any insite or experience with these systems. It is made by Fulton Thermal Corp.

Cory McKnight
Design Engineer
ACCO Engineered Systems
1700 Industrial Road
San Carlos CA 94070
Tel: 650-631-5977
Fax:650-594-4915

 


Replies:

Yooper22

66.96.96.94

"Re(1):emergency heat" , posted Fri 6 Feb 16:52user profileedit/delete messagepost reply


Ball park figure answer is in the question. 150 Tons X 12,000 = aproximate heat rejection. That ball park figure would be around 1,800,000 BTU's per hour at or near full load.

BS is biodegradeable Truth is not.

 

 

energy

4.62.166.19

"Re(2):emergency heat" , posted Wed 12 Jan 15:49user profileedit/delete messagepost reply


It is customary to add 10-20% on the figure above. and if it is an absorbtion chiller you may want to chech with the factory, it's much more.