Original message
| ne14rc | "T8611M Connections" , posted Tue 17 Feb 20:10:  
Hello Folks New guy here.
Just purchased this t-stat. I was told it could replace the cheap analog unit which controls a Goodman GMT, N-Gas furnace and heat pump BUT...... It does not work..no display. It is NOT defective as I tried it on my upstairs furnace which is another T8611M.
Connections on old t-stat; R,Y,G and W. Blue is connected at Furnace but was not terminated at T-stat.
Any words of help??
THANKS!!
[this message was edited by ne14rc on Tue 17 Feb 20:31] | | Replies:
|
| Xenos Webmaster 
| "Re(1):T8611M Connections" , posted Tue 17 Feb 20:15  
That is a heat pump thermostat and requires a common wire. You may be able to get it running by connecting this blue to the common on both the thermostat and the furnace.
Xenos.
The best way to escape a problem is to solve it.
|
| | Xenos Webmaster 
| "Re(3):T8611M Connections" , posted Tue 17 Feb 20:33  
Make sure you have 24vac between R and C if you do the thermostat is defective.
R= power C= common
Xenos.
The best way to escape a problem is to solve it.
|
| | Xenos Webmaster 
| "Re(5):T8611M Connections" , posted Tue 17 Feb 20:44  
Don’t know why the difference with the W to E but I know you need the R and C.
Xenos.
The best way to escape a problem is to solve it.
|
|
|