"Compressor locked up" , posted Wed 31 Mar 19:46user profileedit/delete messagepost reply


Got a service call, went to the site and found out the compressor was locked up. Breaker did not trip. So I shut off the service and wait for it to cool down. Hours later, I put the power on. The compressor never start up and it did trip the breaker. It is a low temp 2 hp 220vac single phase. Now, is there any trick I can get this baby to start up again? I didn't have a chance to check for short yet. I think it might be shorted to ground internally.

 


Replies:

Xenos
Webmaster



69.156.59.208

"Re(1):Compressor locked up" , posted Wed 31 Mar 20:41user profileedit/delete messagepost reply


If it's single phase, add a hard start cap in parelle with the run cap.


http://www.123supply.com/spsupbooshar1.html

Xenos.

The best way to escape a problem is to solve it.

 

 

beginner

68.173.41.90

"Re(2):Compressor locked up" , posted Thu 1 Apr 20:47user profileedit/delete messagepost reply


The compressor was internally shorted. I replaced it today.

 

 

Xenos
Webmaster



67.70.16.73

"Re(3):Compressor locked up" , posted Fri 2 Apr 07:08user profileedit/delete messagepost reply


Cool, their normaly grounded or siezed.