Snce this is a power stealing thermostat you may need to install a 270 10 watt resistor between W and common at the furnace.
Xenos.
The best way to escape a problem is to solve it.
|
| | Xenos Webmaster 
| "Re(3):Chronotherm III T8600 C1014" , posted Sat 10 Apr 17:10  
OOPS I was asuming you had the thermostat powered. -AC means it's not powered.
Make sure your reading 24vac between R and W.
Xenos.
The best way to escape a problem is to solve it.
|
| | Xenos Webmaster 
| "Re(5):Chronotherm III T8600 C1014" , posted Sun 11 Apr 09:13  
OK I’m baffled the current draw is good and it should work. Now I have never saw a furnace with a 40 vac control system and that thermostat is designed for 24vac maby this is the reason.
P.S. the R wire is connected to R and not RC correct?
Look here and note the control modules it will not work with, maybe you have one of these modules and it’s the 40 vac thing.
http://hbctechlit.honeywell.com/techlit/PDF/69-0000s/69-0339.pdf
Xenos.
The best way to escape a problem is to solve it.
|
| | Xenos Webmaster 
| "Re(3):Chronotherm III T8600 C1014" , posted Sat 10 Apr 15:34  
It puts a load on the thermostat witch causes curent to leak through the W terminal and thus powering the thermostat. Most furnaces can do it some require a resistor.
It should be listed in the back of the manual.
Xenos.
The best way to escape a problem is to solve it.
|
| | Xenos Webmaster 
| "Re(4):Chronotherm III T8600 C1014" , posted Sun 11 Apr 15:46  
What ignition control does the furnace have? Look it up in the table.
No you cannot put 24 vac on R to W as the reading your getting through W is a finding a potential difference through the module and is not common.
Now you could power R and have W powering a relay with the other side of the relay connected to the transformers common.
Xenos.
The best way to escape a problem is to solve it.
|
| | Xenos Webmaster 
| "Re(6):Chronotherm III T8600 C1014" , posted Sun 11 Apr 17:49  
This thermostat does not require a common as long as there is enough leakage (potential difference) caused by current flow. If there isn’t a resistor needs to be installed between W and C at the furnace.
Xenos.
The best way to escape a problem is to solve it.
|
| | Xenos Webmaster 
| "Re(8):Chronotherm III T8600 C1014" , posted Tue 13 Apr 20:42  
The only specs they give for the resistor is 270 ohm at 10 watts
Xenos.
The best way to escape a problem is to solve it.
|
| | Xenos Webmaster 
| "Re(10):Chronotherm III T8600 C1014" , posted Fri 16 Apr 18:20  
Common is the opposite side of that low voltage transformer. One side is power the other is common.
Xenos.
The best way to escape a problem is to solve it.
|
| | javelli | "Re(2):Re(10):Chronotherm III T8600 C1014" , posted Tue 11 May 15:56  
Finally I found the solution. My furnace did not give the right voltage. I am not sure if it is AC or DC or some mix of it. In any case the thermostat needs pure AC. I now bought an AC adaptor which feeds the thermostat. In this circuit I put an AC relay which switches the furnace now. When the thermostat switches to 'heat on', the boiler starts. Thanks for your support and tips !!
|
|
|