Original message
| rgsamsel 
| "Oil pressure" , posted Wed 21 Jul 22:35  
How does the johnson control oil psi switch work and how do you trouble shoot or test it?
| | Replies:
|
| Xenos Webmaster 
| "Re(1):Oil pressure" , posted Wed 21 Jul 22:40  
It looks for a pressure differential, if the pressure difference does not occur in 90 Seconds the switch will open. To test it, I kill power to the compressor and keep the control circuit energized. If the contactor does not de-energize in 90 – 120 seconds the oil pressure control is either wired wrong or is defective.
Xenos.
The best way to escape a problem is to solve it.
|
|
|