| icemate | "York Rooftop 0 Suction , 150 Hi Side , 5,5A" , posted Sat 24 Jul 20:59  
Full charge of 7#7oz put in w/scale Suction 0 psi , Hi Side 150 psi , RLA 5.5A. New Compressor, same results Suspected bad piston - Clean Filter, Evap fan working properly any advice welcomed
Icemate
| | Replies:
|
| icemate | "Re(1):York Rooftop 0 Suction , 150 Hi Side " , posted Sun 1 Aug 18:39  
problem solved. Open TXV. Changed valve and everything works fine. When wide open, there was no load. Thanks
Icemate
|
| Will Robinson | "Re(1):York Rooftop 0 Suction , 150 Hi Side" , posted Sun 25 Jul 01:10  
Definitely look for a restriction like Brandman said.
|
| brandman | "Re(1):York Rooftop 0 Suction , 150 Hi Side " , posted Sat 24 Jul 21:23  
Sounds like you got a restriction. Theres a screen in the liquid line on a lot of those small York rooftops. You usually have to pull the top because the liquid line runs over the top of the blower. If its there it'll be labeled