"2 pipe chiller humidity" , posted Sat 2 Oct 08:39user profileedit/delete messagepost reply


Is there a way of "scrubbing" the humidity out of a two pipe chiller system; the humididy that blows in is about 75%

robert e haskell

 


Replies:

Chiller guy

152.163.100.195

"Re(1):2 pipe chiller humidity" , posted Sun 3 Oct 21:37user profileedit/delete messagepost reply


If you are trying to lower the humidity in the space it may require reheating the air. The humidity off the cooling coil will be close to 100% so you have to mix the air or reheat to lower the humidity. If you can check it on a Psychrometric chart you can see what is required to acheive a given condition.

What was the temperature of the air at 75% RH ? Is this a CV or VAV system?

Good Luck

All refrigerants are safe - All refrigerant are dangerous. The difference is YOU !!!

 

Xenos
Webmaster



69.156.2.216

"Re(1):2 pipe chiller humidity" , posted Sat 2 Oct 10:37user profileedit/delete messagepost reply


Scrubbing as in a desiccant wheel? Depending on your application there are several commercial dehumidifiers on the marker for industrial use.

Xenos.

The best way to escape a problem is to solve it.

 

 

Gary Lloyd

216.234.101.23

"Re(2):2 pipe chiller humidity" , posted Tue 7 Dec 14:12user profileedit/delete messagepost reply


What are the drybulb and wetbulb temps of the entering and leaving air? What are the entering and leaving water temps?