Lenox pilot won't light (G776RGD-10) - http://www.hvacmechanic.com/ Forums


Original message

skier722

69.136.159.233

"Lenox pilot won't light (G776RGD-10)" , posted Sun 12 Dec 08:13user profileedit/delete messagepost reply


I have a Lenox furnace with the G776RGD-10 Intermittent control module and the pilot will not ignite without manual lighting. I do hear the module clicking like it wants to light but it doesn't.
I have also replaced the sparker but it still will not light.
Do you think it is the control module itself?
If so I have the G776RGD-10 module and all I can find is the G776RGD-14C which they say will work.
Will this work and will it most likely solve my problem?
Thanks,
Joe

Thanks
Joe

 


Replies:

Xenos
Webmaster



67.71.23.228

"Re(1):Lenox pilot won't light (G776RGD-10)" , posted Sun 12 Dec 12:06user profileedit/delete messagepost reply


I'm not sure what will replace it but I do know they get weak and the spark just isn't strong enough to fire up.

Xenos.

The best way to escape a problem is to solve it.

 

 

skier722

69.136.159.233

"Re(2):Lenox pilot won't light (G776RGD-10)" , posted Tue 14 Dec 19:33user profileedit/delete messagepost reply


Thank you. It looks like the replacement module fixed the problem. The ignitor throws a uch stronger spark. So far so good.

Thanks
Joe

 

 

skier722

69.136.159.233

"Re(2):Lenox pilot won't light (G776RGD-10)" , posted Sun 12 Dec 14:51user profileedit/delete messagepost reply


It sounds like your saying it probably is the control module getting weaker thus not giving off a good spark. Is that right? So getting a new one should fix the problem.

Thanks
Joe