Microbubbles and Tap dancing - http://www.hvacmechanic.com/ Forums


Original message

chiller guy

152.163.100.198

"Microbubbles and Tap dancing" , posted Thu 16 Dec 20:02user profileedit/delete messagepost reply


To whom it may concern:

To this point I am unable to find any chiller qualified service tech or design engineer who is fixated or even aware of a microbubble related problem with these (or any) chiller. There are many conditions that could cause the problem mentioned and they vary to an extent with chiller make and model. Until convinced otherwise I suspect a little tap dance is being used until the real problem is discovered. I've seen it performed before.
I gather that this problem is happening to a unit in Canada but they are essentially the same as those in the U.S.

All refrigerants are safe - All refrigerant are dangerous. The difference is YOU !!!

 


Replies:

Gary Lloyd

216.234.126.169

"Re(1):Microbubbles and Tap dancing" , posted Sat 18 Dec 13:55user profileedit/delete messagepost reply


I generally ask for a list of temperatures, which will clearly reveal most problems, but rarely does anyone provide these. We can only "see" the system through the description and the data.

Unfortunately, most people would rather guess at what is wrong, with as few clues as possible. It's a variation on the old "Name That Tune" game show on TV, minus the prize.

Condenser air/water in temp
Condenser air/water out temp
Saturated condensing temp (from P/T chart)
Liquid line temp near condenser
Liquid line temp near metering device

Evaporator water/air in temp
Evaporator water/air out temp
Saturated suction temp (from P/T chart)
Suction line temp near evaporator
Suction line temp near compressor

________________________

Gary R. Lloyd CMS
HVACR Troubleshooting Books/Software
Written by a veteran Service Technician

https://www.merchantamerica.com/tmethod/