"Pressures and temps" , posted Tue 21 Jun 20:50user profileedit/delete messagepost reply


I had a problem today. Unit wasn't cooling as it should. It's a 15 ton York, 3 compressors, (2 tandom, 1 single). The tandom pair was showing suction pressure @about 96 psi, 55-60 degrees. Discharge pressure was 225 degrees, about 108 degrees. Ambient temp was 108 degrees. Probable cause? I need help on this one.
GilbertC

We are what we are and that's what we are!

 


Replies:

MasterTech



68.95.238.240

"Re(1):Pressures and temps" , posted Tue 21 Jun 22:40user profileedit/delete messagepost reply


You have no Super heat and no sub cool. May have more then one problem. Did make sure the filter and coils where clean. Since this must be a TXV system I personally would add freon until i had atleast 6degree of sub cool. Then recheck it.

 

TechMaster



70.118.15.173

"Re(1):Pressures and temps" , posted Tue 21 Jun 22:07user profileedit/delete messagepost reply


It sounds like one of the tandem compressors isn't running at full capacity. It may have bad valves or not running at all. The discharge pressure seems low for that suction pressure if the compressors were running 100%.