| nhtess | "york condenser fan" , posted Wed 20 Jul 15:30  
Have a York condensing unit where the fan cycles on and off. Compressor is running and unit seems to be holding temp fine but seemed unusual for fan to cycle on and off every 45 seconds or so. any info. would be appreciated.
| | Replies:
|
| OldTech | "Re(1):york condenser fan" , posted Sat 23 Jul 11:10  
Sounds like your condenser may have a Low Ambient Kit installed. This allows the Condenser to cool under low ambient (low outdoor temperature) conditions. Some of the low ambient kits vary the condenser fan speed while others use a high pressure switch(closing on pressure rise) that will cut the fan on with a high pressure of perhaps 280psig and fan off at 190psig.
|
| Xenos Webmaster 
| "Re(1):york condenser fan" , posted Wed 20 Jul 17:07  
Clean the condencer as it may be overheating... '
Xenos.
The best way to escape a problem is to solve it.
|
| | nhtess | "Re(2):york condenser fan" , posted Wed 20 Jul 19:05:  
Thank you, have that planned for morning.will let you know. I wasn't sure if there was some kind of cycling switch on the unit. Marc.
[this message was edited by nhtess on Wed 20 Jul 19:35] |
|
|