"york condenser fan" , posted Wed 20 Jul 15:30user profileedit/delete messagepost reply


Have a York condensing unit where the fan cycles on and off. Compressor is running and unit seems to be holding temp fine but seemed unusual for fan to cycle on and off every 45 seconds or so.
any info. would be appreciated.

 


Replies:

OldTech

24.49.41.94

"Re(1):york condenser fan" , posted Sat 23 Jul 11:10user profileedit/delete messagepost reply


Sounds like your condenser may have a Low Ambient Kit installed. This allows the Condenser to cool under low ambient (low outdoor temperature) conditions. Some of the low ambient kits vary the condenser fan speed while others use a high pressure switch(closing on pressure rise) that will cut the fan on with a high pressure of perhaps 280psig and fan off at 190psig.

 

Xenos
Webmaster



65.94.118.32

"Re(1):york condenser fan" , posted Wed 20 Jul 17:07user profileedit/delete messagepost reply


Clean the condencer as it may be overheating...
'

Xenos.

The best way to escape a problem is to solve it.

 

 

nhtess

24.147.222.105

"Re(2):york condenser fan" , posted Wed 20 Jul 19:05:user profileedit/delete messagepost reply


Thank you, have that planned for morning.will let you know.
I wasn't sure if there was some kind of cycling switch on the unit.
Marc.