I m having trouble with a rooftop unit .When you turn it on the comp starts and cools for almost 90 seconds and than it stops cooling and you hear a venting sound as pressure is relieving inside.is there a internal relief valve in the comp or a bypass valve for hi pressure somewhere in the system.or is the compressor bad and leaking thru.

[this message was edited by tg2 on Sat 30 Jul 14:01]

 

Replies:

MasterTech



68.95.138.204

"Re(1):help on roof top comfort unit" , posted Sat 30 Jul 16:54user profileedit/delete messagepost reply


Yes. its in the compressor. If it goes off it means that the head pressure is too high for some reason. Reason are over charged, bad fan motor, restriction and so on.

 

 

tg2

66.168.174.89

"Re(2):help on roof top comfort unit" , posted Sat 30 Jul 18:30:user profileedit/delete messagepost reply


its not over charged and the fan is working and the coils are clean ,do you have anymore suggestions to check.what else causes this ? thanks for you response

[this message was edited by tg2 on Sat 30 Jul 18:30]

 

 

Xenos
Webmaster



69.156.2.92

"Re(3):help on roof top comfort unit" , posted Sun 31 Jul 11:02user profileedit/delete messagepost reply


What is the head pressure?

Xenos.

The best way to escape a problem is to solve it.

 

 

MasterTech



68.95.132.135

"Re(3):help on roof top comfort unit" , posted Sat 30 Jul 19:35user profileedit/delete messagepost reply


Then you have either a restriction or a bad high pressure bypass.
What type of sub cool and super heat do you get. Can you get pressures right off the compressor?

 

 

freon john

209.82.163.136

"Re(4):help on roof top comfort unit" , posted Sat 30 Jul 20:58user profileedit/delete messagepost reply


internal presuure reliefs have been know to go bad and relieve at a lower pressure. what kind of pressures are you running?

try then and try harder

 

 

tg2

66.168.171.166

"Re(5):help on roof top comfort unit" , posted Sun 31 Jul 16:44:user profileedit/delete messagepost reply


thanks to all, it was indeed the compressor.it was relieving so quick i could not get a good pressure reading.replaced compressor and alls well.

[this message was edited by tg2 on Sun 31 Jul 16:45]

 

 