| JLW | "Noisy Compressor, Low Suction" , posted Thu 4 Aug 15:58  
I found the Geothermal plastic line to the field was nearly dry so the pump was overheating and not pumping water to the exchanger. This made everything overheat and cause bad pressures and kickouts. Thanks for suggestions
JLW
| | Replies:
|
| sheetmetalkid | "Re(1):Noisy Compressor, Low Suction" , posted Thu 30 Aug 20:57  
when you had your leak air lock went to your circ pump when the fancoil was calling for it to pump from your feild it kicked out on a safety feature so it wouldn't overheat find the leak which is probably at one of your fusion links on the loop itself
|
| sheetmetalkid | "Re(1):Noisy Compressor, Low Suction" , posted Thu 30 Aug 20:51  
how much leaked out?
|
| Xenos Webmaster 
| "Re(1):Noisy Compressor, Low Suction" , posted Thu 4 Aug 16:05  
I can’t believe none of us picked up on a water cooled condenser, however now it’s so obvious when you read “geothermal heat pump”
Xenos.