"TRANE OUT ON LOW PRE." , posted Sat 7 Jan 11:33user profileedit/delete messagepost reply


MODEL TWA120A300B COOLING MODE WORKS FINE BUT WHEN GOING INTO HEAT IT WILL RUN FOR ABOUT A MINUTE OR TWO THEN SHUT OFF ON LOW PRESSURE. I DID NOTICE FREEZING AT THE CHECK VALVES. COULD THIS BE THE PROBLEM?? THANKS FOR ANY INPUT.

 


Replies:

ashton

208.3.11.114

"Re(1):TRANE OUT ON LOW PRE." , posted Sat 14 Jan 14:50user profileedit/delete messagepost reply


no it is not a water source heat pump. i have a txv valve ordered for it and check valve, im hoping this takes care of the problem. thanks for the input.

 

BostonMech

204.94.119.201

"Re(1):TRANE OUT ON LOW PRE." , posted Fri 13 Jan 19:59user profileedit/delete messagepost reply


Is this a water-source heat pump? If so, check strainer on condenser coil. If partially or fully plugged, it will cause the unit to trip out on low pressure or freeze protection during the heating mode and possibly high pressure in cooling mode.