lzheng

65.93.201.253

"Air cooled condenser indoor installation" , posted Sun 8 Jan 14:29user profileedit/delete messagepost reply


I have a walk in cooler(20'W x 30'H x 7'H) installed in a high celling(18' high) warehouse, the air cooled condenser is install on roof top, the cooler can't work very well in winter. Is it possible to move the condenser into the warehouse, maybe on the top of the the cooler? Is there any building code to consider?

 


Replies:

Freezone12



72.64.104.71

"Re(1):Air cooled condenser indoor installatio" , posted Sat 28 Jan 14:34user profileedit/delete messagepost reply


quote:
Is it possible to move the condenser into the warehouse, maybe on the top of the the cooler?

restaraunts do it all the time.

_______________________________________
If it don't fit
force it.
If it breaks
it needed to be replaced anyways.

 

Archangel

66.26.61.160

"Re(1):Air cooled condenser indoor installatio" , posted Mon 23 Jan 14:42user profileedit/delete messagepost reply


You can also add ductwork to the discharge side of the condensing coil and run the duct to exhaust to the outside.
But this will leave you with some service issues like cleaning the coil and replacing the condensor fan motor when that time comes.

Assistant Trades Supervisor HVAC
17 years exp.
Licensed

 

pacserve

208.63.254.63

"Re(1):Air cooled condenser indoor installatio" , posted Sun 8 Jan 18:03user profileedit/delete messagepost reply


Forgot to add this. The manufacturer of unit can size the proper parts. If you move indoor what about the other seasons?

 

pacserve

208.63.254.63

"Re(1):Air cooled condenser indoor installatio" , posted Sun 8 Jan 18:00user profileedit/delete messagepost reply


What you need to do is install a head pressure regulating control. This will shut off outdoor motor to keep pressure up and in extreme cases bypass condensor coil.