sir i need you comment on this, i have a split type air con with 2 evaporator controlled by 2 TXV,(ALCO TCLE 300 HW 100) and this is my parameter,

suction press 52 psig
Disch press 250 psig
Liquid temp 95.8 fahr
gas temp 63.2 fahr
Superheat 34.8 fahr
subcool 20.7 fahr

compressor
amp:
Line 1 12.1
Line 2 12.1
Line 3 12.7

Volt
AB 375
BC 377
AC 373

is my system OK, flooded or starving? please i need your comment i've been close monitoring this unit for 2 days now, cant afford to loose this unit i dont have any back up. thank you!

 


Replies:

Chiller guy

205.188.117.5

"Re(1):a/c parameter" , posted Mon 9 Jan 19:54user profileedit/delete messagepost reply


First off your drier is trash. If you pulled it out and blew air through it and then reinstalled it, you may have introduced water into the system.

Second the superheat looks awfully high. Which valve is this reading for?

What refrigerant are you using? what is your supply voltage?

This system needs to have someone on site to check it out. Is there anyone you can hire to help you out?

All refrigerants are safe - All refrigerant are dangerous. The difference is YOU !!!

 

jbmendoza

210.14.44.170

"Re(1):a/c parameter" , posted Sun 8 Jan 23:19user profileedit/delete messagepost reply


by the way outdoor temp is 91.8 fahr.

 

 

theapprentice

68.167.84.246

"Re(2):a/c parameter" , posted Mon 27 Feb 16:50user profileedit/delete messagepost reply


It appears to be a restriction. But I'm not sure. I never heard of a unit that ran at 375 volts. You should definitely call someone with experience.

Good day!