"centrifical fans" , posted Wed 11 Jan 12:49user profileedit/delete messagepost reply


Can someone please tell me if I have a commercial centr.fan and the downstream chilled water coils are changed to a different fins per inch, thus creating a less restricted downstream air flow, would/could that create an extream increase/vacuum on the suction side of the fan. I understand if the downstream side is closed off a centrifial fan will just sit there churning away, creating heat but not moving any air, but what about no downstream restriction?

 


Replies:

chiller guy

64.12.116.199

"Re(1):centrifical fans" , posted Wed 11 Jan 16:04user profileedit/delete messagepost reply


Think of the fan as an "Air Pump". The fluid it pumps is air and acts like a water pump. If there are no, or little restrictions they both pump their hearts out (will overload). However; if you restrict the flow (valves, dampers,coils, filters, etc.)the flow drops off accordingly. Thus the need for air balance or water balance!
A more important question is how changing the fins per inch (why?) will affect the capacity of the coil?

All refrigerants are safe - All refrigerant are dangerous. The difference is YOU !!!