Original message
| mgtbeck | "Honeywell Chrontherm III reading" , posted Sat 17 Jun 14:06  
Hi,
Sorry can't find the manual. Read out says -AC and don't seem to getting any connection from thermostat to unit. No heat, no AC, no manual fan. Replaced batteries last month. Suggestions? What does that readout mean? Thanks.
Brian
| | Replies:
|
| qbeanie | "Re(1):Honeywell Chrontherm III reading" , posted Thu 6 Jul 21:45  
I just had the same problem. The control fuse on the 24 volt control board was blown. $1.28 at ace hardware and 1/2 labor to troubleshoot.
|
| acefurnacefixer 
| "Re(1):Honeywell Chrontherm III reading" , posted Sat 17 Jun 16:48  
-ac means the t-stat is running off the batteries, there is no power to the unit.
Yes! I CAN fix that! Excuse my spelling......I am paid to fix it not spell it. Music is meant to be heard not felt......TURN DOWN THE BASS!