Honeywell Chrontherm III reading - http://www.hvacmechanic.com/ Forums


Original message

mgtbeck

24.49.73.176

"Honeywell Chrontherm III reading" , posted Sat 17 Jun 14:06user profileedit/delete messagepost reply


Hi,

Sorry can't find the manual. Read out says -AC and don't seem to getting any connection from thermostat to unit. No heat, no AC, no manual fan. Replaced batteries last month. Suggestions? What does that readout mean? Thanks.

Brian

 


Replies:

qbeanie

68.3.1.110

"Re(1):Honeywell Chrontherm III reading" , posted Thu 6 Jul 21:45user profileedit/delete messagepost reply


I just had the same problem. The control fuse on the 24 volt control board was blown. $1.28 at ace hardware and 1/2 labor to troubleshoot.

 

acefurnacefixer



70.226.1.52

"Re(1):Honeywell Chrontherm III reading" , posted Sat 17 Jun 16:48user profileedit/delete messagepost reply


-ac means the t-stat is running off the batteries, there is no power to the unit.