2-30 ton cond units screwed up - http://www.hvacmechanic.com/ Forums


Original message

actech4u



69.113.199.200

"2-30 ton cond units screwed up" , posted Sun 18 Jun 20:12user profileedit/delete messagepost reply


Found 2- 30 ton trane cond (running for 6 years)units that had many problems
1 shipping brackets left on
2 no pump down solenoids installed
3 1 t-stat that energized terminals 1+3
4 1 t-stat in the cond unit that had a discharge air temp sensor mounted infront of evap coil, but was suposed to be a return air sensor.
5 2nd stage compressors when wires are put back on control box high side pressure goes to 400+ off on internal
6 forgot to mention all safety controls jumped out.
I put solenoid in but I question return & discharge air temperatur sensors do they have to be installed ?
The 2nd t stat in the cond unit (dc Voltage) should be located in the space but does the trane cond unit have to have that stat?

ACTECH4U

 


Replies:

chiller guy

205.188.116.139

"Re(1):2-30 ton cond units screwed up" , posted Tue 20 Jun 17:45user profileedit/delete messagepost reply


Model # and Serial # please

All refrigerants are safe - All refrigerant are dangerous. The difference is YOU !!!

 

 

actech4u



69.113.199.200

"Re(2):2-30 ton cond units screwed up" , posted Thu 22 Jun 18:56user profileedit/delete messagepost reply


trane m # raucc30ecw13000 s # c02g06201

ACTECH4U