Found 2- 30 ton trane cond (running for 6 years)units that had many problems 1 shipping brackets left on 2 no pump down solenoids installed 3 1 t-stat that energized terminals 1+3 4 1 t-stat in the cond unit that had a discharge air temp sensor mounted infront of evap coil, but was suposed to be a return air sensor. 5 2nd stage compressors when wires are put back on control box high side pressure goes to 400+ off on internal 6 forgot to mention all safety controls jumped out. I put solenoid in but I question return & discharge air temperatur sensors do they have to be installed ? The 2nd t stat in the cond unit (dc Voltage) should be located in the space but does the trane cond unit have to have that stat?
ACTECH4U
| | Replies:
|
| chiller guy | "Re(1):2-30 ton cond units screwed up" , posted Tue 20 Jun 17:45  
Model # and Serial # please
All refrigerants are safe - All refrigerant are dangerous. The difference is YOU !!!
|
| | actech4u 
| "Re(2):2-30 ton cond units screwed up" , posted Thu 22 Jun 18:56  
trane m # raucc30ecw13000 s # c02g06201