This is a 208/3/60 contactor with a 24vac coil on a Lennox 5 ton
furnace/Condensing unit. With an initial 22.6vac available, just as the call for CU to act the voltage drops to 15vac and the contactor chatters and fails to engage. With a manual boost to the contactor it engages and the compressor starts and continues to run. Old contactor did same as the new one just installed. The thermostat is a single stage mercury bulb on cooling. On 3 other identical systems, 22.6 volts works fine.
1.) Should 22.6vac be enough to pull in a 24vac coil?
2.) On a call for cooling, what could cause the voltage to drop
to 15vac.
3.) Are contactors with a 24vac coil used much today?

(Yes, we removed all items between call for cooling and the contactor coil: IE: anti-recycle-timer, high pressure cutout, etc, on the low-voltage circuit.)

To err is human to repair divine

 


Replies:

jimhermansen

207.6.199.237

"jimhermansen" , posted Wed 9 Aug 21:47user profileedit/delete messagepost reply


try jumpering R and Y at the furnace. If the trans. is dropping to 15volts, this will not close the contactor. try a new tx or looj for bad connections.

jimher