Contactor Chatter - http://www.hvacmechanic.com/ Forums


Original message

Dog Biscuit

207.200.116.67

"Contactor Chatter" , posted Sat 24 Jun 19:10user profileedit/delete messagepost reply


This is a 208/3/60 contactor with a 24vac coil on a Lennox 5 ton
furnace/Condensing unit. With an initial 22.6vac available, just as the call for CU to act the voltage drops to 15vac and the contactor chatters and fails to engage. With a manual boost to the contactor it engages and the compressor starts and continues to run. Old contactor did same as the new one just installed. The thermostat is a single stage mercury bulb on cooling. On 3 other identical systems, 22.6 volts works fine.
1.) Should 22.6vac be enough to pull in a 24vac coil?
2.) On a call for cooling, what could cause the voltage to drop
to 15vac.
3.) Are contactors with a 24vac coil used much today?

(Yes, we removed all items between call for cooling and the contactor coil: IE: anti-recycle-timer, high pressure cutout, etc, on the low-voltage circuit.)

To err is human to repair divine

 


Replies:

weber

64.12.117.69

"Re(1):Contactor Chatter" , posted Sun 16 Jul 23:22:user profileedit/delete messagepost reply


check for 24v right out of the transformer, if you have it there check for it at the stat,(red wire)if you have it jumper your red and your yellow, that should send 24 to the contactor. Check it, if you have it you have to much restitance in the stat, change the stat goto a digital, get away for the merc ones. they sell cheap easy to use digital stats that are simple to use and install. some use batteries and others use a common!

[this message was edited by weber on Thu 30 Oct 21:25]

 

thechiller

205.188.116.139

"Re(1):Contactor Chatter" , posted Thu 29 Jun 22:46user profileedit/delete messagepost reply


Have you checked the transformer, (all 24v transformers are not the same) you should have at least a 40 va (volt/amps)transformer or you can get a volt drop as the different coils energize.

Service you can trust

 

Dog Biscuit

207.200.116.67

"Re(1):Contactor Chatter" , posted Sat 24 Jun 23:45user profileedit/delete messagepost reply


Xenos--- What am I doing wrong to cause triplication of my post.

To err is human to repair divine

 

 

Xenos



65.93.116.38

"Re(2):Contactor Chatter" , posted Sun 25 Jun 15:30user profileedit/delete messagepost reply


No idea...

Xenos.

The best way to escape a problem is to solve it.

 

Xenos



65.93.116.38

"Re(1):Contactor Chatter" , posted Sat 24 Jun 19:40:user profileedit/delete messagepost reply


As well as the stat. This could be a bad wire/ connection or a weak transformer.

Xenos.

The best way to escape a problem is to solve it.

[this message was edited by Xenos on Sat 24 Jun 19:42]

 

fitter597



67.165.168.193

"Re(1):Contactor Chatter" , posted Sat 24 Jun 19:39user profileedit/delete messagepost reply


it's the mercury t-stat dropping your voltage i bet.

LOCAL 597 PIPEFITTERS
"We Do It Right The First Time"

 

 

SMOKEmadBLUNTS



68.83.240.106

"Re(2):Contactor Chatter" , posted Sun 25 Jun 14:14user profileedit/delete messagepost reply


rooftop?,split? u probably have a shorted control, if its a rooftop look at everything in the cooling circuit like the economizer controls ect.....

Please save the applause till the end
Nate Certified
EPA certified
Specialize in water cooled heat pump buildings
Master Mechanic for a small Commercial/Industrial service only outfit

 

 

Dog Biscuit

207.200.116.67

"Re(3):Contactor Chatter" , posted Sun 25 Jun 19:11user profileedit/delete messagepost reply


Feedback and follow-up to my Question:
Your suggestion that the mercury bulb T'stat was questionable prompted us to jumper it---and the control-voltage went from 15vac to 19. Then we placed a jumper in the control panel that isolated both the t'stat and the wires to the t'stat---and the voltage jumped to 26.2vac. Now the contactor is 'slamming-in" the way it should.
Our conclusion is that during a remodel the t'stat wires were compromised. Thank you for the loyal support---DB

To err is human to repair divine

 

 

GEOGY KENNY

218.18.184.102

"Re(4):Contactor Chatter" , posted Sun 23 Jul 22:51user profileedit/delete messagepost reply


Saswell Group (HK) Ltd is a growing company engaged in products including manufacture of thermostats, electric zone valves, and modulating valves for HVAC applications. We are selling our product both under our own brand name and on OEM bases. We have developed strong relationships with many international companies in the HVAC industry. Our goal is to help our customers and partners to improve their business performance and market penetration.
No mater you are a manufacturer, a distributor, or a contractor, we are ready to provide you with our good quality products and professional services. No mater what your need is digital programmable thermostats or non-programmable thermostats, electric zone valves or modulating valves, Saswell is a brand name trusted by contractors for our product quality and reliability.
You can get more information about our company and our products from our website: www.saswell.com , or you can just contact me by email: salesone@saswell.com. We are always willing to discuss with you about your need.

We SASWELL is the main manufacturer handle in thermostat and valves . If you are interesting please visit our web www.saswell.com to learn more.

 

 

hvac

138.26.224.160

"Re(5):Contactor Chatter" , posted Tue 19 Sep 15:07user profileedit/delete messagepost reply


I agree with the contactor coil is starting to short out. This would drop your voltage and will blow the control fuse eventually. I have also install a shunt across the coil and it has stopped the chattering before. You can buy them at a electroic store its just a filter.

 

 

harpo

141.157.214.7

"Re(6):Contactor Chatter" , posted Mon 25 Sep 20:03user profileedit/delete messagepost reply


always check the rooftop or slit at the rooftop terminal strip as you found,on new units that are being strated up always read the secondary at the TR. manufacturers always tap for the hi voltage when its a 200/208/240 primary go for the 2 lowest even if your reading 210V tap for the 200V and that little more on the secondary!

It ain't going to get any lighter looking at it!