"hvac rooftop unit" , posted Fri 11 Aug 00:03user profileedit/delete messagepost reply


water drips down into my building through my unit when it rains

is my unit missing a drainage pan ?

runner

 


Replies:

hvac

138.26.224.160

"Re(1):hvac rooftop unit" , posted Tue 22 Aug 16:09user profileedit/delete messagepost reply


Sounds like you are leaking from around the Curb of the unit.

 

chiller guy

152.163.100.132

"Re(1):hvac rooftop unit" , posted Fri 11 Aug 11:27user profileedit/delete messagepost reply


"Only when it rains". Check all the roof penatrations, make sure the electricians did not drill through the drain pan to run conduit.

All refrigerants are safe - All refrigerant are dangerous. The difference is YOU !!!

 

kevink

65.54.155.57

"Re(1):hvac rooftop unit" , posted Fri 11 Aug 07:37user profileedit/delete messagepost reply


No it is not missing a pan but could be cracked perhaps. I would suspect a blockage in the condensate drain line over the above. While you or somone else does it, also check your filter. Make sure it is clean as is the evaporator coil.

 

 

fitter597



67.165.168.193

"Re(2):hvac rooftop unit" , posted Sun 17 Sep 22:29user profileedit/delete messagepost reply


electricians are the biggest calprits when it comes to RTU's leaking in the rain, they drill thru the bottom curb and the unit and it's hard to seal that area and I have heard many issues about that, but only when it rains.
I know what Chiller guy is talking about.