Someone remind me !!!!!! - http://www.hvacmechanic.com/ Forums


Original message

kopec_wayne

64.114.107.41

"Someone remind me !!!!!!" , posted Sat 23 Sep 22:04user profileedit/delete messagepost reply


Been away from refrigeration service for quite some time and school even longer than that .............. to test for superheat I know you take your suction # and covert to a temp, take the temp @ the txv bulb, subtract the 2 and WALA, your superheat of the evap, low= to aprox - 4-6, medium = 8-10 and high temp= 12-15 degree's. Subcooling ? how to measure and what are the approx values ?

THANKS

The Fridge GUY !!!!

 


Replies:

heatingman

76.16.135.3

"Re(1):Someone remind me !!!!!!" , posted Tue 26 Sep 22:56user profileedit/delete messagepost reply


Subcooling is found by taking liquid pressure conerting to temp. and subtracting the physcal liqiud line temp. 8-10 degrees is good if you have over 18 remove some juice under 5 clean the coils or add juice.

hope this helps

 

beginner

70.18.209.133

"Re(1):Someone remind me !!!!!!" , posted Sun 24 Sep 19:13user profileedit/delete messagepost reply


http://www.refrigtech.com/charge.html
Hope this help.