Original message
| kopec_wayne | "Someone remind me !!!!!!" , posted Sat 23 Sep 22:04  
Been away from refrigeration service for quite some time and school even longer than that .............. to test for superheat I know you take your suction # and covert to a temp, take the temp @ the txv bulb, subtract the 2 and WALA, your superheat of the evap, low= to aprox - 4-6, medium = 8-10 and high temp= 12-15 degree's. Subcooling ? how to measure and what are the approx values ?
THANKS
The Fridge GUY !!!!
| | Replies:
|
| heatingman | "Re(1):Someone remind me !!!!!!" , posted Tue 26 Sep 22:56  
Subcooling is found by taking liquid pressure conerting to temp. and subtracting the physcal liqiud line temp. 8-10 degrees is good if you have over 18 remove some juice under 5 clean the coils or add juice.