"York Diamond 80 dead blower by Emily Latella" , posted Sun 5 Nov 10:36user profileedit/delete messagepost reply


10 year old diamond 80 has no blower running either heat or AC. just replaced gas valve to solve an ignition problem. a week later woke up to a cold house and a popped breaker - reset and the blower won't kick in. replaced the capacitor first. still won;t start. hear a click from the board after burner ignition. system runs for 2 mins and then kicks off. windings test ok. the motor spins freely.
i get 4 flashes from the board LED which says "out of limit"


hey - i just jumped the motor - it's fine. the board has a large burn spot on it...

never mind.

Zoom

 


Replies:

Zzz

205.250.200.46

"Re(1):York Diamond 80 dead blower by Emily La" , posted Fri 8 Dec 01:23user profileedit/delete messagepost reply


Hook 110v to the blower if it runs change the limit which I dought needs changing since that would make the blower run continuous.