I have a paint booth that will not go to high fire. i do not have much experiance with these units. its a jbi model cfa20
is the air damper interlocked with the high fire? can anyone tell me the sequence of operation there is no manuals. thanks

gasfitter level 1 apprentice
gasfitter level 2 certified

Its the things u learn after u think u know it all.

 


Replies:

Zzz

205.250.200.46

"Re(1):Spray booth" , posted Fri 8 Dec 01:00user profileedit/delete messagepost reply


These units go into high fire after 10 minures of low fire there is a dip on the board that we have been using to eliminate low fire. Or there is the option of jumping out W1` and w2 to get high fire right away. Are you running a 2 stage t-stat?If not F low fire and jump w-1 and w-2. 2 stage to me is stupid.