Bryant Roof Top Package - http://www.hvacmechanic.com/ Forums


Original message

the blur

67.100.8.23

"Bryant Roof Top Package" , posted Mon 11 Dec 15:11user profileedit/delete messagepost reply


I just started working on Bryants. 10 ton package.
The LED on the control board flashing 7 times, but I didn't have the manual. So it took me 3 hours to find a bad roll out switch.
Where can I get a factory service manual? The owners-installation manual on the job site was not helpful at all.

Also, with the bad roll out switch, The blower is locked on. The vent motor is locked on, and the A/C is locked out.
Why does Bryant do this ???

HVAC Mongar

 


Replies:

86project

205.188.116.139

"Re(1):Bryant Roof Top Package" , posted Tue 12 Dec 02:23user profileedit/delete messagepost reply


www.hvacpartners.com
You will have too register with the site,

If you give me a email address I can email you one of fax one too you
Or you can call carrier out OF the dallas tx don't have a phone number need too look it up , tell them you need a manual

Check YOUr heat exchanger ,, when the roll out switch opens up Heat exchanger may be bad, If you get a call back DOUBLE check the exchanger