| psycheus | "Trane 60 Ton Chillers?" , posted Sat 16 Dec 23:30  
Anyone have any experenice on these? Having problems with circuit 2 compressor getting an error saying it's tripping the breaker killing the unit, however the breakers aren't tripped.
Rick aka psycheus
http://gallery.psycheus.com http://www.tacnit.com http://forum.drc.su
| | Replies:
|
| dbcooper | "Re(1):Trane 60 Ton Chillers?" , posted Thu 18 Sep 16:46  
trane also has a high side sensor that controls condenser fans, if the valve after sensor is not front seated slightley-- no pressure is read by sensor --therfore cond fans will not kick on and compressors will go off on high head
|
| chiller guy | "Re(1):Trane 60 Ton Chillers?" , posted Sun 17 Dec 20:25:  
Sounds like an "Intellipak" control unit but need model & serial to know exactly what you have. Model is a big help. New unit to you? Any repairs? Entire unit shutting down or just one circuit? Suspect unit has two circuits, each containing two 15 ton Trane scroll compressors, correct?
All refrigerants are safe - All refrigerant are dangerous. The difference is YOU !!!
[this message was edited by chiller guy on Sun 17 Dec 20:28] |
| harpo | "Re(1):Trane 60 Ton Chillers?" , posted Sun 17 Dec 18:22  
how about a unit model number,and those CBs have a micro switch behind the breaker(CB may be up but the micro is open) that is within that control circuit...need to know what UCP controller is on the unit(blue LEDS/black or HI tan panel yellow screen) and what style compressors
It ain't going to get any lighter looking at it!
|
|
|