"flames go on and off" , posted Tue 23 Jan 17:27user profileedit/delete messagepost reply


working on a Lennox rooftop. the thermostat calls for heat then the unit starts working. somewhere in between the flames must go off. I open the panel and the flames come back on. The highest temp it gets in the room is 62 degrees. What is causing this problem? I hear the unit igniting itself over again.

 


Replies:

cool p

70.39.0.136

"Re(1):flames go on and off" , posted Tue 23 Jan 21:37:user profileedit/delete messagepost reply


I just ran into the same problem and it was the flame rod senser give it a try

I AM WORKING ON A RHEEM ROOFTOP UNIT AND THERE IS NO HEAT 5 TONS 120000 BTUS I HAVE POWER TO THE INDUCER FAN MOTER BUT THE FAN NO WORK PLEASE HELPME

[this message was edited by cool p on Tue 23 Jan 21:44]

 

 

Antonetz

65.24.201.55

"Re(2):flames go on and off" , posted Tue 13 Feb 11:55user profileedit/delete messagepost reply


if you have an ohm's meter, unplug motor at quick connect an you should have continuity through the motor windings. if not replace motor. Antonetz r. p. hope this helps, let me know.

R.P.Antonetz

 

tom446



66.67.27.228

"Re(1):flames go on and off" , posted Tue 23 Jan 17:39user profileedit/delete messagepost reply


Just a guess, but maybe it's going out on limit. The best place to start would be to check and make sure you filters and evaporator coil are clean. Also check for cracked heat exchangers.

If in doubt call a pro !

 

 

cedric

67.173.128.84

"Re(2):flames go on and off" , posted Fri 2 Feb 17:18user profileedit/delete messagepost reply


I checked all limits and the filters. I then replaced the limits. It still goes off on the limit at the tube heat exchanger. It seems like there is some sort of a restriction but I can't find it The temp gets to 69, which isn't bad but the customer wants it warmer.

 

 

tom446



66.67.27.228

"Re(3):flames go on and off" , posted Fri 2 Feb 19:07user profileedit/delete messagepost reply


where is this limit located that keeps going out

If in doubt call a pro !

 

 

cedric

67.173.128.84

"Re(4):flames go on and off" , posted Wed 7 Feb 23:02user profileedit/delete messagepost reply


the limit at the tube heat exchanger. I checked to see if it was cracked but I didn't see anything.

 

 

marchvac



64.231.244.252

"Re(5):flames go on and off" , posted Thu 7 Feb 13:21user profileedit/delete messagepost reply


What is model and serial#

Be careful sometimes you don't get a second chance

 

 

rickmcd72

68.196.19.48

"Re(5):flames go on and off" , posted Wed 28 Feb 17:55user profileedit/delete messagepost reply


Your problem is the heat exchanger, its either cracked or rotted-

Rick

 

 

Antonetz

65.24.201.55

"Re(5):flames go on and off" , posted Tue 13 Feb 11:48user profileedit/delete messagepost reply


i recently had almost the same problem, replace flame sensor or remove & steel wool. insure with thermometer that heat exchanger temps. are as designed temp. rise through unit, s.a vs r.a. check flames for roll out when blower kicks on, note: this indicates a bad heat exchanger, insure your themostat anticipator is properly set & you are not losing 24v signal from thermostat. Antonetz r.p. hope this helps, let me know.

R.P.Antonetz