I have a 1987 Rheem gas furnace and I am replacing the blower motor. The motor has seven wires: black, blue, white, brown/white, brown, yellow, and red. My furnace has black, red and white. I am trying to connect the motor (3/4 hp 115v), run capacitor and furnace. What wires go where?
Thank You
| | Replies:
|
| Antonetz | "Re(1):blower motor" , posted Wed 21 Feb 12:37:  
new motor black[hi speed] blue [med. hi speed] yellow [med. low speed] red [low speed] the two browns\white go to new capacitor. then connect what speed you want for cooliing & fan on, to the black wire of your furnace, & the speed you want for heating mode to the red wire of you furnace, [white to white,[common]note cap off other unused leads. if after you connect speeds, check air flows & if you don;t like swicth to another speed.
R.P.Antonetz
[this message was edited by Antonetz on Wed 21 Feb 12:39] |
| | nygiants7 | "Re(2):blower motor" , posted Fri 23 Feb 17:41  
thank you, it worked. But what was difficult to understand was that the white wire from the furnace was originally connected to the capacitor from the old motor.