Hi Techs, I have a 1ton Carrier unit that tripps the breaker every time its energized. Wondering where to start looking for the problem.

Anthony Bullock

 


Replies:

fire and ice

67.174.44.160

"Re(1):Tripping Breakers" , posted Wed 25 Apr 00:44user profileedit/delete messagepost reply


If you are tripping your high voltage breaker. My first instinct says grounded compressor. Check the 3 compressor legs to ground.

 

theduke03

68.9.215.192

"Re(1):Tripping Breakers" , posted Tue 27 Mar 18:17user profileedit/delete messagepost reply


If you're speaking of the breaker for your outdoor unit, most likely your compressor is locked or grounded.You can try installing a hard-start kit to assist compressor at startup.

Be safe

 

bretster

68.251.102.105

"Re(1):Tripping Breakers" , posted Tue 27 Mar 18:09user profileedit/delete messagepost reply


Electrical grouding. Check all motors for electrical integrity if the breaker your tripping is high voltage.
Check the control circuit if your tripping your 3.2 amp breaker located in the unit/transformer.