Hi Techs, I have a 1ton Carrier unit that tripps the breaker every time its energized. Wondering where to start looking for the problem.
Anthony Bullock
| | Replies:
|
| fire and ice | "Re(1):Tripping Breakers" , posted Wed 25 Apr 00:44  
If you are tripping your high voltage breaker. My first instinct says grounded compressor. Check the 3 compressor legs to ground.
|
| theduke03 | "Re(1):Tripping Breakers" , posted Tue 27 Mar 18:17  
If you're speaking of the breaker for your outdoor unit, most likely your compressor is locked or grounded.You can try installing a hard-start kit to assist compressor at startup.
Be safe
|
| bretster | "Re(1):Tripping Breakers" , posted Tue 27 Mar 18:09  
Electrical grouding. Check all motors for electrical integrity if the breaker your tripping is high voltage. Check the control circuit if your tripping your 3.2 amp breaker located in the unit/transformer.
Hope this helps.
.
|
|
|