"Mitsubishi Mr Slim" , posted Mon 9 Jul 22:50user profileedit/delete messagepost reply


I have a mistsubishi Mr Slim split system heat pump. It's worked fine for 2 years, but all of a sudden it drips from the vents in the indoor unit after it's been running for awhile. I checked the drain hose outside the house and it does NOT seem to be clogged. Any suggestions???? Thanks

 


Replies:

BlueFlame

71.185.43.80

"Re(1):Mitsubishi Mr Slim" , posted Wed 11 Jul 19:44user profileedit/delete messagepost reply


Check the condensate drain line first thing. It's probably clogged.

 

 

BlueFlame

71.185.43.80

"Re(2):Mitsubishi Mr Slim" , posted Wed 11 Jul 19:46user profileedit/delete messagepost reply


I'm assuming that you do see water running from the condensate line outside.

you still may have a partial blockage on the pan inside.