"relays" , posted Sun 19 Aug 15:01user profileedit/delete messagepost reply


what is a way to figure out if a potential or current relay is bad. I ohmed out thw windings - OK, check start and run capacitors - OK but I am not sure hoe to tell if the relay is the problem other than potential relay has a normally closed contact and the current relay has a normally open. All helps apprieciated !!

In the Trade for a long long time !
Things a bit different than before !
Refrigeration still doesn't have a "d" in it does it ?

 


Replies:

kimmy

69.159.231.93

"Re(1):relays" , posted Sun 23 Sep 22:17user profileedit/delete messagepost reply


Get a hard start relay for your compressor.
Bypass the wiring and install it.
Compressor is probably seized.

30+ years in the HVAC/R trade.
Started when equipment was repaired not replaced.
Still feel the same way.

 

bigglenn357



70.21.5.165

"Re(1):relays" , posted Sun 19 Aug 17:17user profileedit/delete messagepost reply


I usually use jumper wires across low voltage on relay and check with meter on ohms to see if continuity is on the ones that are supposed to be normally open they should be closed with voltage and normally closed should read open.

Big Glenn

 

 

Houston204



98.196.66.53

"Re(2):relays" , posted Sun 19 Aug 17:49user profileedit/delete messagepost reply


Measure performance. If the start cap reads within range but you have high starting amperage this would point toward your start relay.

"Tip of the Day" Remember to remove power first.