"Conpressor cold to touch but no error code" , posted Mon 27 Aug 15:01user profileedit/delete messagepost reply


Help!! On a 2 compressor Lennox package unit, what would cause compressor #1 to be cold to the touch but compressor #2 is very warm. The unit has the electronic digital readout but no error codes are displayed. The unit is cooling the facility with no complaints but I know something is wrong.

mtmoriah

 


Replies:

jmitschke



70.113.61.44

"Re(1):Conpressor cold to touch but no error c" , posted Sun 9 Sep 20:58user profileedit/delete messagepost reply


The 1st (warm) compressor is running and pushing freon thru the valves of the 2nd (cold)compressor,thus causing it to cool down...kinda normal on some units...just a possibility...john...austin,texas

 

Gregg Harris

64.12.117.9

"Re(1):Conpressor cold to touch but no error c" , posted Mon 27 Aug 16:21user profileedit/delete messagepost reply


Don't be alarmed, only one compressor runs at a time.

"It takes less time to do something right the first time than it does to explain why you did it wrong."

 

 

marchvac

24.57.145.130

"Re(2):Conpressor cold to touch but no error c" , posted Mon 27 Aug 21:53user profileedit/delete messagepost reply


if the second stage is on and the first stage is not then I would check the high head manual reset. If it has two condenser fans make sure both are working.

 

 

fitter597



67.174.0.159

"Re(3):Conpressor cold to touch but no error c" , posted Mon 27 Aug 22:58user profileedit/delete messagepost reply


March is right check for high head manual reset, if #2 is running #1 failed, could be bad contactor too.