BDP579D blower keeps running - http://www.hvacmechanic.com/ Forums


Original message

thermoheat

75.3.94.25

"BDP579D blower keeps running" , posted Tue 18 Sep 20:46user profileedit/delete messagepost reply


I have a BDP579D rooftop unit. The blower keeps running after the burner shuts off. If I tap the Cam Stat S106 time delay relay,the blower shuts off. I replaced the time delay but I still have the same problem.

 


Replies:

jmitschke



70.113.61.44

"Re(1):BDP579D blower keeps running" , posted Thu 20 Sep 17:41user profileedit/delete messagepost reply


Hey, Did you change the entire cam stat or just the relay? I would change the entire part and make sure it is set around 100-120 degrees as a shut off temp. If the temp is set to low, the blower will turn due to external heat(attic, closet, sunlight etc...)John...austin,texas