"carrier rooftop" , posted Wed 14 Nov 18:16user profileedit/delete messagepost reply


What would be causing the flame rollout switch to keep tripping. Also a very bad odor coming from flue box that burns the eyes

 


Replies:

commtech

24.209.0.212

"Re(1):carrier rooftop" , posted Mon 14 Jan 18:35user profileedit/delete messagepost reply


Carriers are natorious for bad heat exchangers,we call it the 5 yr heat exchanger replacement program where I work.I bet if you take a co reading at the inducer motor discharge it will go off the scale.Carriers are also good for the inducer blower wheel falling apart.

 

 

mtcorey

65.216.254.98

"Re(2):carrier rooftop" , posted Thu 29 May 13:13user profileedit/delete messagepost reply


on the money

 

hvacdan1234

24.63.131.28

"Re(1):carrier rooftop" , posted Thu 22 Nov 06:05user profileedit/delete messagepost reply


first the unit is not burning correctly gas nat or propane your role out is tripping because of high heat flames will not burn correctly thru soot.its safty devise. check or remove heat exchanger and clean make sure flame retainers and all plates are in there get a cut sheet from manufacturer

20 years in trade

 

amech

68.251.178.144

"Re(1):carrier rooftop" , posted Wed 14 Nov 19:41user profileedit/delete messagepost reply


Sounds like you may have a bad heat exchanger. Does the flame rollout at start up or when main blower energizes? model & Serial would be helpful.

 

 

mtcorey

64.136.26.227

"Re(2):carrier rooftop" , posted Wed 14 Nov 22:06user profileedit/delete messagepost reply


Its a carrier weathermaker model 48dr601350. The flame does rollout at first. Could it maybe the flue tubes need cleaned because they look pretty bad.

 

 

marchvac



24.57.145.130

"Re(3):carrier rooftop" , posted Thu 15 Nov 21:35user profileedit/delete messagepost reply


Sounds like a bad heat exchanger.

Be careful sometimes you don't get a second chance

 

marchvac



24.57.145.130

"Re(1):carrier rooftop" , posted Wed 14 Nov 19:40user profileedit/delete messagepost reply


What is the model and serial. Is it propane or nat. If the unit is belt drive where the motor is there is a panel below it. Remove that panel and check if there is a crack in heat exchanger.

Be careful sometimes you don't get a second chance