| Fatzo757 | "Changed thermostat" , posted Tue 18 Dec 12:09  
I have installed a new RTH7500 on a ruud heat pump system, I labled that wires and connected everything, the A/C will work but the heat will not work. The fan will automaticly start and stop.
Original stickers and wireing: R - Red B - Blue G - Green Y - Yellow W2 - White X - Brown
Currently inside the thermostat after copying another setup i thought was the same. Red wire to (RC jumped to R) Orange wire to o/b Yellow wire to y Green to g blue to c black wire to E white wire labled (W2) to Aux
Inside the heat pump there are only five connectors
R - Red B - Blue Y - Yello D - White C - Brown G - Not Connected O - Not connected
Any help would be greatful. Also the heat pump is a Ruud RQNJ
| | Replies:
|
| Houston204 
| "Re(1):Changed thermostat" , posted Wed 19 Dec 01:36  
New terminal = wire C = brown G = green Y = yellow O/B = blue Rc & R = red Aux = white E = jumper to Aux (unless you verify that black is in use at your fancoil, you didn't list it in your original wiring)
Option 170 = 7 option 190 = 1
"Tip of the Day" Remember to remove power first.
|
| | fatzo757 | "Re(2):Changed thermostat" , posted Wed 19 Dec 06:25  
Thank you will try.
|
|
|