Condenser Problems - http://www.hvacmechanic.com/ Forums


Original message

hvacmicmac

216.9.188.146

"Condenser Problems" , posted Wed 16 Jul 19:46user profileedit/delete messagepost reply


This unit won't start on it's own. It is a Yorkie heat E1RA pump new install by another company. It may be wired wrong (Power or Thermostat) but the 24v is not getting to the contactor. The Def Board has been replaced. I have jumpered the 24v from the Thermostat red to the contactor and that will make it run So the contactor is good. But it is running in heat mode that way. Any ideas on this issues???

Heavy D

 


Replies:

oldmangobles

64.85.145.187

"Re(1):Condenser Problems" , posted Sat 19 Jul 11:03user profileedit/delete messagepost reply


is there 24v at Y to common in a call for cool?can you get to t-stat and wire R to Y and G to test t-stat?does this unit run properly in heat mode?

old man mike