75 ton Trane intellipak DX - http://www.hvacmechanic.com/ Forums


Original message

HP3

72.88.131.249

"75 ton Trane intellipak DX" , posted Thu 17 Jul 16:18user profileedit/delete messagepost reply


Unit runs fine until 1 of 2 compressor circuit's trips out. Then the space pressure rises from .05 to .30. Thru the Tracer BMS I reset manual diagnostics several times until area stabilizes. 3 active diagnostics are pending: automatic reset, ckt1 comp. trip and RA Rel humid fail.
Any insight's ?

 


Replies:

Chiller Guy

205.188.117.9

"Re(1):75 ton Trane intellipak DX" , posted Sat 19 Jul 16:32:user profileedit/delete messagepost reply


Are you reading the diagnostics from the Tracer display or from the RTU display?
The auto reset diagnostic should say more,like "SA static Pressure Limit". This shows the the SA pressure exceeded the limit setpoint which will shut down the SA fans, close the IGV's, and shutdown the compressors. After an "autoreset" everything will restart.
The RA Rel Humid (sensor) fail indicates the sensor input is out of range. Check wiring and connectionsbetween the sensor and the ECEM.
The air pressure is probably taking down the compressors instead of the other way around. Check the SA Static Pressure setpoints.

Good Luck

All refrigerants are safe - All refrigerant are dangerous. The difference is YOU !!!

[this message was edited by Chiller Guy on Sat 19 Jul 16:34]

 

dwcaveney



68.125.196.195

"Re(1):75 ton Trane intellipak DX" , posted Sat 19 Jul 15:17:user profileedit/delete messagepost reply


perimeter or interior loop? how many VAVs? the relief air damper is modulating toward closed? Indoor positive P is going from 12.5 pascals to 75?

DW

[this message was edited by dwcaveney on Tue 22 Jul 01:38]

 

Jojo98

69.246.153.58

"Re(1):75 ton Trane intellipak DX" , posted Sat 19 Jul 14:47user profileedit/delete messagepost reply


What type of compressors? And what do you mean by space pressure?