| harpo | "Re(1):cannot maint. room temp. & chiller trip" , posted Wed 15 Oct 19:45  
the chiller should have a chilled water setting on the controller for itself...4F-45F is typical for the chiller loop dependinng on the style of chiller control you might have a setting to match the lenght of the loop.the setting is considered a reaction to what is coming back to it on the return and how the chiller reacts with cyclying off compressors or keeping them on.model number if possible.then the settings on a 3 air handlers if the rooms have their own dedicated stat and chiller control......and the biggest design factor is it a 3-way valve on the air handler(s) the chiller has to see constant flow as if it was just a straight run with no air handlers.if you have in-line control valves,and the spaces satisfy and the water shuts off to the zone. how does the water get back to the chiller,and the flow switch might be shutting you down.
It ain't going to get any lighter looking at it!
|
| Jojo98 | "Re(1):cannot maint. room temp. & chiller trip" , posted Fri 10 Oct 23:43  
First, Your terminology is difficult to understand. Second, If you could provide: Unit M/N and S/N, Alarm codes, and chiller pressures and temperatures, that would help significantly. If the chiller is oversized, and it is locking out on low cooler temp. Then I agree. Also, If you are working with a Carrier representitive, then the only equipment they go to school for and work on is Carrier equipment. I would heed their advice, especially if they have phyically seen the chiller package.
|
|
|