Original message
| bigglenn357 
| "liebert t-stat pass code" , posted Mon 27 Oct 19:11  
Subcontractor installed ceiling hung unit in mri room before I was there well this liebert tstat needs a passcode 3 numbers,to change temp settings anyone know if there is a generic override code or how to reset?Thats why I do all in house work now so shit doesnt get lost!! Its set to 68 degrees and needs to be at 73 degrees the patients are freezing while getting zapped!! Thanks for any info
Big Glenn "Imagination is more important than knowledge" (Albert Einstien)
| | Replies:
|
| bigglenn357 
| "Re(1):liebert t-stat pass code" , posted Tue 28 Oct 19:51:  
Well just fyi codes are 123 and 321 also to disable codes altogether dip switches on back of tstat #8 turn to on to disable codes Thanks hvacben I found # to tech support I just disabled the damn passcodes
Big Glenn "Imagination is more important than knowledge" (Albert Einstien)
[this message was edited by bigglenn357 on Tue 28 Oct 19:53] |
| hvacben | "Re(1):liebert t-stat pass code" , posted Tue 28 Oct 19:49  
try 123 or 321 i've worked on these units before in many data centers and if that doesn't work try 000
|
|
|