York Rooftop - http://www.hvacmechanic.com/ Forums


Original message

suretempchris

69.156.90.154

"York Rooftop" , posted Thu 30 Oct 08:34user profileedit/delete messagepost reply


#9 Fault reads Ignition control lockout/ignition control failure /Limit switch trip/ . This fault comes up in cooling also. York tech says the safties are monitored at all times in these units. Recommended jumping 24v from R to limit contact. Did this still faulting. Have done all that York tech recommened. Still faulting. Put up two units at same time one ok. Other constant faults.This is a problem that York is aware of.

Refrigeration Mechanic/Gas Tech 1

 


Replies:

Jojo98

152.86.133.139

"Re(1):York Rooftop" , posted Thu 30 Oct 12:09user profileedit/delete messagepost reply


Take the ignition control to the operating unit, hook it up and see if you get the same fault. If you do, purchase a new ignition control.

 

 

suretempchris

69.157.110.124

"Re(2):York Rooftop" , posted Fri 31 Oct 08:35user profileedit/delete messagepost reply


Ignition control has been changed.

Refrigeration Mechanic/Gas Tech 1