| juan_tambay | "approach........." , posted Sun 2 Nov 13:59  
hi guyz....can you explain what is co-relation between condenser and evaporator approach.....
thanks to all...
sonny lazo
| | Replies:
|
| Jojo98 | "Re(1):approach........." , posted Sun 2 Nov 22:46  
There isn't a relationship between the. They have nothing to do with on and the other. It is a measurement between the condenser leaving water temp and saturated liquid refrigerant temp. Also, chill water leaving temp and saturated suction refrigerant temp. Usually a narrow difference is wanted. A wide band is an indicator that there is a problem with the water or refrigerant circuit, much like subcooling and superheat.
|
|
|