WR 50A50 6 flashes? - http://www.hvacmechanic.com/ Forums


Original message

dwflood

216.192.137.134

"WR 50A50 6 flashes?" , posted Tue 18 Nov 10:59:user profileedit/delete messagepost reply


I think the flame probe on my furnace is defective. The unit will start (draft inducer runs), HSI heats up and gas valve opens, gas ignites but the gas valve closes right away. The control module gives a 6 flash LED diagnostic code. This cycle will repeat a few times then usually operates normally for awhile afterwards. The installation manual only lists diagnostic codes up to 5 flashes (White/Rodgers 50A50-110). Anyone know what 6 means? Thanks.

[this message was edited by dwflood on Tue 18 Nov 11:22]

 

Replies:

Xenos
Webmaster



67.71.21.100

"Re(1):WR 50A50 6 flashes?" , posted Tue 18 Nov 18:19user profileedit/delete messagepost reply


What is the make and model of the furnace ?

Xenos.

The best way to escape a problem is to solve it.

 

 

dwflood

152.163.253.1

"Re(2):WR 50A50 6 flashes?" , posted Tue 18 Nov 21:31user profileedit/delete messagepost reply


Its a 'Comfortmaker RPJ II' manufactured by Inter-City Products (their model number is GUI075A012BIN). The control is a White Rodgers 50A50-110. The gas valve shuts off just a second or two after ignition, maybe a failing flame probe? 6 flashes of the LED. thx.

 

 

Xenos
Webmaster



67.71.21.100

"Re(3):WR 50A50 6 flashes?" , posted Tue 18 Nov 21:45user profileedit/delete messagepost reply


Yes I would agree, Try sanding it up.

Xenos.

The best way to escape a problem is to solve it.

 

 

rgshotswell

12.73.68.98

"Re(4):WR 50A50 6 flashes?" , posted Sun 29 Feb 12:27:user profileedit/delete messagepost reply


Kudos
I also have a Intercity furnace with the identical problem that is shutting down a few seconds after ignition 6 blinks. I did as you instructed cleaning the heat probe. I NOW HAVE HEAT.
THANK YOU

[this message was edited by rgshotswell on Sun 29 Feb 12:31]

 

 

mcharis23

68.42.228.59

"Re(5):WR 50A50 6 flashes?" , posted Fri 11 Feb 11:09user profileedit/delete messagepost reply


I also have a Comfortmaker Furnace with the same problem. Could you tell me where the Heat Probe is located?

Thank you.

M.

 

 

Mastertech



68.95.177.75

"Re(6):WR 50A50 6 flashes?" , posted Fri 11 Feb 16:22user profileedit/delete messagepost reply


Should be left burner, Has i single white wire connected to it. It is a steel rod. Little sand or use steel wool.

 

 

rgshotswell

12.74.233.8

"Re(5):WR 50A50 6 flashes?" , posted Sun 7 Mar 21:26user profileedit/delete messagepost reply


Melaman:

Went to your website to give you my city and state. Apparently you already have take the liberty to attach a city and state to my name. Unforunately you are wrong. I am not from Elgin, Illinois. Dallas is more like where I am from.
Next time be sure before you leap.

Kudos
I also have a Intercity furnace with the identical problem that is shutting down a few seconds after ignition 6 blinks. I did as you instructed cleaning the heat probe. I NOW HAVE HEAT.
THANK YOU

 

 

melaman



64.230.160.219

"Re(6):WR 50A50 6 flashes?" , posted Sun 7 Mar 22:41user profileedit/delete messagepost reply


Thank you for your reply. I had received a few replies at the same time and mistakenly posted the incorrect city.
My apologies, the mistake has been corrected.
If you do not want to be listed on our feedback page please let us know and I will remove that segment.
I hope we may be of help to you in the future.
Again, thanks for visiting
Melaman

Pareto's Law
If a group of tasks are arranged in order of their priority 80% of the value come from the top 20% of the list.

 

 

melaman



64.230.160.219

"Re(5):WR 50A50 6 flashes?" , posted Mon 1 Mar 23:19user profileedit/delete messagepost reply


I'm glad we could be of service to you. We would like to use your comments on our feedback page. http://www.hvacmechanic.com/feedback.htm
Would you mind sending us what city & state you are from. You can post your reply or send it to me at -
melaman@heatingandairconditioninghelp.com

Thank you for your help

Melaman
HVAC Mechanic.com

Pareto's Law
If a group of tasks are arranged in order of their priority 80% of the value come from the top 20% of the list.

 

 

leewill

65.26.83.203

"Re(6):WR 50A50 6 flashes?" , posted Wed 6 Jun 19:53user profileedit/delete messagepost reply


Ok guys, I've got the 6 flashes and I just replaced the flame sensor. I am still getting the 6 flashes.
One thing that is different than what's been talked about is that I am trying run my AC, not my furnace.
The blower will not start up, but the condensor (outside unit) seems to be working fine.
Anyone have any ideas???

Thanks for any replies.