| purseljb | "Honeywell T8611R wiring" , posted Fri 12 Dec 13:31  
I just purchased a Honeywell T8611R to replace my Trane Weathertron BAYSTAT240A. The current wiring diagram is; R-red, T-brown (this connection is attached to the screw holder and goes through the board and goes to the mercury switch),O-orange, G-green, Y-yellow, X2-black, B-blue, W-white (this connection is attached to the screw holder and goes through the board and goes to the mercury switch and is also jumpered to what looks like a "J" with a 1 in it), F-empty. The Honeywell has; R, C, O, B, G, W2, E, W1, Y1 (currently jumpered to W1), L, and P. I'd hate to ruin the new thermostat. I'd really appreciate any assistance that can be offered. Thanks in advance, Jack
Jack
| | Replies:
|
| xenos Webmaster 
| "Re(1):Honeywell T8611R wiring" , posted Fri 12 Dec 17:24  
The connections are as follows
Honeywell.
R- Power C- Common B- Reversing valve heating O- Reversion valve cooling G- Fan W2- Aux heat E- emergency Heat W1 and Y1 – compressor
Trane bay stat 240A
R-Power B-Common O- Reversion valve cooling G-Fan X2-Wmergency heat W- Aux heat Y- Compressor
All others are not required
For more information refer here.
http://www.hvacmechanic.com/tstatwiring.htm
Xenos.