When the Tempstar AirConditioner from the attempts to power on the 3 amp fuse on the Furnace blows and the air conditioner does not turn on. My Father In-Law moved one of the red wires when he was at the residence last time and it worked so he left. Now the same thing is happening again as soon as he walks out the door. The manual says that this is due to the 24v Wiring, I suspect that it is the way I have it wired although it could also be a short according to the manual. Anyone know if we wired this right?
Initial Wiring I Diagramed at http://acallegiance.freeservers.com/FurnaceTerminals.GIF
FYI, to get to this link you will have to copy and paste it into the browser address bar, doesn't support clicking on it from here.
[this message was edited by Idaho Jay on Mon 14 Jun 11:10] | | Replies:
|
| xenos Webmaster 
| "Re(1):Payne PG8DAA Furncace 3 AMP Fuse Blows" , posted Mon 14 Jun 17:29  
is this only during a call for cooling?
Xenos.
The best way to escape a problem is to solve it.
|
| | Idaho Jay | "Re(2):Payne PG8DAA Furncace 3 AMP Fuse Blows" , posted Mon 14 Jun 18:22  
Yes, this is only durring a call for cooling.
|
| | Xenos Webmaster 
| "Re(3):Payne PG8DAA Furncace 3 AMP Fuse Blows" , posted Mon 14 Jun 20:35  
check the compressor contactor then.
Xenos.
The best way to escape a problem is to solve it.
|
| | Idaho Jay | "Re(4):Payne PG8DAA Furncace 3 AMP Fuse Blows" , posted Sat 19 Jun 19:38  
I have tested the compressor contactor and it seemed OK. I don't have a 24 V to check the magnetic switch, but it worked with our car battery charger. The fuse blows but the switch never triggers.
|
| | Cinder | "Payne PG8DAA" , posted Mon 14 Jun 23:35  
I don't know if this will be relevant, but I have had the same issue with Goodman units 24Volt wiring, I have had the same occur when then neutral off the transformer was connected to the rest of the neutrals instead of it's designated spot on the circuit board. It's given me browm boards to just a blown fuse.
|
| | Idaho Jay | "Re(1):Payne PG8DAA" , posted Sat 19 Jun 19:41  
I don't see anything like that. All the wires are going into the insert plugs except the 24 volt wiring that I have diagramed.
|
| TexasTech | "Re(1):Payne PG8DAA Furncace 3 AMP Fuse Blows" , posted Mon 14 Jun 04:06  
You have damaged thermostat wires, most likely @ the outdoor unit. Moving them apart so they don't touch each other works for a while till it rains. The stat wire either needs to be fixed or a new one ran.
|
| | Idaho Jay | "Re(2):Payne PG8DAA Furncace 3 AMP Fuse Blows" , posted Mon 14 Jun 11:08  
I will check the cables when I go onsite later and replace them. I will start with the external air conditioner thermostat wires at your recommendation TexasTech. So this diagram that I drew out is wired correctly?
|
| | Idaho Jay | "Re(3):Payne PG8DAA Furncace 3 AMP Fuse Blows" , posted Sat 19 Jun 19:32  
The cables were VERY tattered. I replaced them but it did not impact the symptoms.
|
|
|