"what electrical do I need for 3 ton Trane?" , posted Tue 29 Jun 20:53user profileedit/delete messagepost reply


Going to have a basic 3 ton Trane system installed (XB-10, model #2TTB0036A)

I need to know what kind of electrical I need. I know I need (or should have) a dedicated 220 line, but I'm not sure what amp for the new disconnect? I'm confused because I hear they are rated for certain amps (30) but I've also heard of "overcurrent", so I want to make sure I get it straight.

If it's dedicated, can I assume I just get the amps the condensor is rated for (I think 30 amps), since nothing else will be on that 220 line?

 


Replies:

Cinder



66.66.117.41

"what electrical do I need for 3 ton Trane?" , posted Tue 29 Jun 21:02user profileedit/delete messagepost reply


A 30 AMP circuit is fine, but it must be dedicated to the condenser. If there are any special power requirements it will be in the installation guide and the sales rep would (should) have made that known.

Save the cost of a service call...Check the "DUMB STUFF" FIRST!!!!!