Original message
| juancarlosc | "Honeywell T8195B to Hunter 44260" , posted Mon 18 Oct 22:19:  
The wires in the wall are:
green, blue, yellow, red and white.
In the Honeywell each one is in the right letter white in W, red in R, etc. W and Y are jumped and nothing is plug in O and C.
How should I connect those wires in the Hunter? The cooler is working but I have no heater when I connect the blue one to RC
Hunter 44260 y1, w/b, y/o, rh, rc, g
help!!!!
JC
[this message was edited by juancarlosc on Mon 18 Oct 22:20] | | Replies:
|
| xenos Webmaster 
| "Re(1):Honeywell T8195B to Hunter 44260" , posted Mon 18 Oct 22:27  
B connects to B since your old W and Y were jumpered put both wires on Y. Ps. Rc and Rh also get jumpered.
Xenos.
The best way to escape a problem is to solve it.
|
| | xenos Webmaster 
| "Re(2):Honeywell T8195B to Hunter 44260" , posted Mon 18 Oct 22:28  
P.S. make sure to switch it to heatpump mode.
Xenos.
The best way to escape a problem is to solve it.
|
| | juancarlosc | "Re(3):Honeywell T8195B to Hunter 44260" , posted Mon 18 Oct 23:16  
I changed to this way:
Green in G Red in RH (Rc and Rh jumped) white and yellow in Y/O blue in W/B Y1 empty
Heat mode
Heating System Selector: HG System Selector: Heat Pump Auto Recovery: enable
The unit turn on but the air is still cool.
?????
JC
|
| | xenos Webmaster 
| "Re(4):Honeywell T8195B to Hunter 44260" , posted Mon 18 Oct 23:26  
Put white and yellow in Y1. But I have to ask why do you have a white and yellow together ? can you please tell me that size of the breaker is serving the air handler. you may have had the wrong thermostat origionaly and can save some money by breaking up the yellow and white.
This is a heat pump correct?
Xenos.
The best way to escape a problem is to solve it.
|
| | juancarlosc | "Re(5):Honeywell T8195B to Hunter 44260" , posted Mon 18 Oct 23:52  
Thank you! Now the heater is working. Tomorrow I will try the A/C and I will post the specs of the equipment. I can't find a flashlight right now.
Thank you again
JC
|
|
|