"Bryant 90 plus" , posted Sun 7 Aug 17:18user profileedit/delete messagepost reply


I was changing the t-stat and now i have a code 24 it is secondary voltage fuse is open check for short circuit in secondary voltage (24v) wiring including thermostat leads disconnect thermostat leads to isolate short circuit. Can you help me? How do i clear the code from the furance?

 


Replies:

tick

65.189.135.29

"Re(1):Bryant 90 plus" , posted Sun 7 Aug 19:06user profileedit/delete messagepost reply


Thank you so very much it is working just fine. You saved me one big headache!

 

MasterTech



68.95.186.254

"Re(1):Bryant 90 plus" , posted Sun 7 Aug 18:07user profileedit/delete messagepost reply


I looked it up what is means is that u blew the 3 to 5 amp fuse on the control board. If u feel that u have T-stat wired corectly then replace fuse with no more than a 5 amp fuse.
Happens when touched the T-stat wires together and still had power to furnace. Should be an automotive type fuse and what ever you do DO NOT REPLACE WITH FUSE BIGGER THEN 5 AMP.

 

tick

65.189.135.29

"Re(1):Bryant 90 plus" , posted Sun 7 Aug 17:40user profileedit/delete messagepost reply


What does that problem mean i have tried to take off t-stat and leave off. I guess i don't understand the error.

 

MasterTech



68.95.186.254

"Re(1):Bryant 90 plus" , posted Sun 7 Aug 17:36user profileedit/delete messagepost reply


Once you have fixed the problem turn T-stat off and turn power off to furnace wait 1 minute and turn back on. Should be cleared by then if board is ok and you fixed problem.