have system 3.5 for compressor 5 for air handler. have been told so many things from so few companies, don't know what to do. have been told i need 5 ton comp and 5 ton handler for 2600 sq home, ft. myers fl. now i'm told i just need 3.5 and 3.5 in lennox system. there should be an easier way i'm sure but ya just don't trust everyone today. Thanks for any help Tony

 


Replies:

rustymike

209.161.202.171

"Re(1):tonnage" , posted Tue 16 Aug 14:02user profileedit/delete messagepost reply


You could use the 5 tr air handler but should make sure that you have the 3.5 tr piston/orifice or TXV in the air handler coil so that you'll match the performance of the outdoor unit.
You should also reduce the fan speed down to medium or med-low to give you the correct airflow through the cooling coil.
your cooling down time will be a bit longer, but you'll also benefit from more moisture removal with the larger sized coil.
Your superheat will be off a bit, but that can be compensated for without much concern.