Armstrong Ultra V Tech 80.

Heater will initiate fan/blower, ingnition occurs lighting burners for about 15 seconds, then unit flames out.

Unit will do this 2-4 times then create electronic lock-out due to ingnition failure. Flash code 1 time - 6 times.

I can shut off breaker, and furnace will try again, with same results.

What needs to be replaced or checked?

Thanks

 


Replies:

tinner73



67.173.164.201

"Re(1):Armstrong Ultra V Tech 80" , posted Thu 1 Feb 21:16user profileedit/delete messagepost reply


clean the flame sensor

union trained in Chicago

 

 

SSAP

68.97.182.117

"Re(2):Armstrong Ultra V Tech 80" , posted Thu 1 Feb 21:52user profileedit/delete messagepost reply


Thank You,

I removed the flame sensor and cleaned it.

Furnace is working fine now.

 

 

Trampas

66.146.209.177

"Re(3):Armstrong Ultra V Tech 80" , posted Sat 12 Jan 12:17user profileedit/delete messagepost reply


Hello SSAP--

Where is the flame sensor on this model? I have the same problem.

 

 

tinner73



68.60.236.253

"Re(4):Armstrong Ultra V Tech 80" , posted Sat 12 Jan 12:51user profileedit/delete messagepost reply


looks like a nail and sits in the flame path. clean with a fine steel wool. not too hard.

union trained in Chicago